Yes, The Panel(s) are fed with Rigid Metal Conduit (RMC) and all loads from the panel are also run in RMC.
If so, it already has an equipment grounding conductor as RMC is allowed to be used as an EGC.
Is there anything in the code that we can reference with respect to this?
As well as being code approved it is also worth noting that RMC is a better equipment ground than any copper wire you could stuff in it.Is there anything in the code that we can reference with respect to this?
As well as being code approved it is also worth noting that RMC is a better equipment ground than any copper wire you could stuff in it.
Are bond bushings required when using a conduit as the EGC? I have not been able to find any requirements in the NEC.
FWIU, during a fault with rmc/emt with a wire type egc pulled, the bonded pipe will actually carry more of the fault current than the wire. All that extra conductive surface makes a great low r path.
As well as being code approved it is also worth noting that RMC is a better equipment ground than any copper wire you could stuff in it.
... How can we determine the adequacy of the existing feeder conduits as EGC's?