I have been asked to look at an older house for sale in Michigan where the receps were not grounded. My question is this: Can GFCI circuit breakers be installed vs a complete rewiring with equipment grounding conductors?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes GFCI protection is one of the NEC approved methods for additional protection of these circuits. What is the wiring method 2-wire, no ground NM cable?
 
Location
Michigan
Occupation
Electrical Contractor
Thank you. I have not inspected it yet. Just going on the potential buyers info. Sales inspection to be performed this week so I'll see what they come back with and then I am meeting the realtor to perform my own inspection. Just thought that GFCI breakers would be a much more affordable option should no ground wire exist. According to the realtor it does have a 100A breaker panel so I would have to assume it has some form of old NM. Not knob and tube!:oops:
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You might note that IF you replace the receptacles and they are in an AFCI required area, the new ones must be AFCI protected.
 