Ungrounded delta systems are very poor choice for electric services. If at all possible, center-side ground one side of the delta. (240/120V and 480/240V are common 3-phase 4-wire delta services used by utilities.) I have seen entire services destroyed because the ungrounded delta is not referenced to ground. A surge on the source side of the service transformer will couple by capacitance through the transformer, raising the voltage on the service to 1000's of volts above ground. Boom. Smoke. Flash.
A ground monitor is good but it requires qualified people to know what it means and troublehooting to find the ground is a pain. We had to shut a whole plant down because one small motor developed a ground and in order to find it we had to turn off one thing at a time until the ground went away. Found another similar when rats nested in a disconnect and their crap created a ground on on phase. Also had an entire lumber mill burn down because two grounds appeared on opposite sides of the plant causing a short that went through the equipment. Not enough current to blow a fuse but enough to cause a fire.
In my opinion, better to blow a fuse.