Forgive me for not having every detail. I hope I have enough to share.
I recently toured a farm that put in a co-generation plant to feed back onto the power companies grid.
When looking at the main power panel that supplied the 480 volt 3 phase power, I noticed that there was no neutral brought to this main panel. I asked the electrician, "why"? He said that the power company was going to give them a closed delta system (no neutral). To run the equipment they didn't need a neutral(all three phase motors).
The electricians installed a step down transformer off two legs of the main to supply lighting and receptacle loads. They also installed 10 ground rods outside in a large loop. I believe the power company did not want to supply this customer with a neutral because they were afraid of stray voltage coming from their lines and affecting the cows? That is only my opinion, because I don't have that great an understanding of the distibution of power as far as the power company is concerned. My concern is that if there were a fault to ground,that the earth would be the path back to the source and that is not good.
I have not yet talked with anyone from the power company, but I would like to. It also appears that there is some voltage flowing on the center tap of this generator that supplies power back to the utility. Probably because the three phases are somewhat unbalanced. This voltage is tied to this ground grid of rods. Since they turned this generator on the cows have been acting a little "funny".
I am interestd to here thoughts on this. Thank you.
I recently toured a farm that put in a co-generation plant to feed back onto the power companies grid.
When looking at the main power panel that supplied the 480 volt 3 phase power, I noticed that there was no neutral brought to this main panel. I asked the electrician, "why"? He said that the power company was going to give them a closed delta system (no neutral). To run the equipment they didn't need a neutral(all three phase motors).
The electricians installed a step down transformer off two legs of the main to supply lighting and receptacle loads. They also installed 10 ground rods outside in a large loop. I believe the power company did not want to supply this customer with a neutral because they were afraid of stray voltage coming from their lines and affecting the cows? That is only my opinion, because I don't have that great an understanding of the distibution of power as far as the power company is concerned. My concern is that if there were a fault to ground,that the earth would be the path back to the source and that is not good.
I have not yet talked with anyone from the power company, but I would like to. It also appears that there is some voltage flowing on the center tap of this generator that supplies power back to the utility. Probably because the three phases are somewhat unbalanced. This voltage is tied to this ground grid of rods. Since they turned this generator on the cows have been acting a little "funny".
I am interestd to here thoughts on this. Thank you.