Ungrounded system (HRG), separately derived system

Status
Not open for further replies.

fatuus

Member
Location
Virginia
Occupation
Electrician
Please help right away.

An HRG grounded xfmr secondary feeds a heat wheel type RTU. I am adding a zig-zag transformer in line to clear harmonics.

It is very difficult to add a grounding electrode to the transformer. I argue that since it is an un-grounded system no GE is necessary.

Am I wrong?
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Please help right away.

An HRG grounded xfmr secondary feeds a heat wheel type RTU. I am adding a zig-zag transformer in line to clear harmonics.

It is very difficult to add a grounding electrode to the transformer. I argue that since it is an un-grounded system no GE is necessary.

Am I wrong?

Sorry, but yes. Also note that this is not ungrounded system-it is a high-impedance grounded system.
 

Ingenieur

Senior Member
Location
Earth
are you saying you have a wye secondary with neutral grounding resistor AND are adding a zig-zag?
do you have a sketch?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
Maybe more fundamentally, if you have devices on the HRG system that are producing harmonics, you may need to rethink the entire setup. Power rectifier systems generally come with surge protection and CM noise mitigation devices that will not like being connected to an HRG system because they are referenced to ground, so they become a lower resistance path than your NGR and try to ground your ENTIRE system until they fail, often catastrophically. You could remove their ground references, but you also reduce their function so the generally recommended practice is to use a Drive Isolation Transformer to feed just those devices, and ground the secondary of that transformer. That could ALSO be a zig-zag isolation transformer if you so desire.
 