An existing plant has a 480 V 3 ph. ungrounded service. The main service equipment in one building feeds 3 ph. power to another building, 1000 feet away (same site). The feeder is 3 wire in non-metallic conduit.
Both buildings (and all other buildings on site) are tied to an extensive 4/0 buried ground electrode system, and also have many other metallic paths (process piping) between buildings. All electrical equipment, panels, etc. are bonded to this electrode system.
The entire facility electrial system is being expanded as part of an overall plant expansion. A new utility service will be installed. Grounded delta or grounded wye supplies are being considered. The existing feeder described above was intended to remain unchanged. Re-looking at this feeder, it looks like 250.32(B)(1) will require a new EGC be run between buildings, with the phase conductors, if the new service is grounded.
Am I reading this correctly?
Both buildings (and all other buildings on site) are tied to an extensive 4/0 buried ground electrode system, and also have many other metallic paths (process piping) between buildings. All electrical equipment, panels, etc. are bonded to this electrode system.
The entire facility electrial system is being expanded as part of an overall plant expansion. A new utility service will be installed. Grounded delta or grounded wye supplies are being considered. The existing feeder described above was intended to remain unchanged. Re-looking at this feeder, it looks like 250.32(B)(1) will require a new EGC be run between buildings, with the phase conductors, if the new service is grounded.