I'm thinking about it from the point of view of why we avoid OCP in the intentionally-grounded conductor unless it opens all conductors.
No conclusions yet, but I feel it's related.
Leaving the corner grounded delta aside for a bit if a single overcurrent device in a grounded neutral system the Grounded Conductor of the circuit becomes energized by the voltage through the loads from the energized conductors. We expect that conductor to be no threat because it is grounded but now we have a possibly deadly set of white, or in other parts of the world black or blue, conductors that are now a hazard to our very lives.
About 3 decades ago I went to do a service call on a home that had once been served by a trolley car line traction power service. That is 600 volts DC. I cannot imagine how the loads were arranged but the original panel had been built by hand. A cabinet was made, lined with asbestos panels, and fitted with porcelain base double pole single throw knife switches with fuses in each line, The 2 conductors laid in the groove at one end of the switches nearest the fuse holder and the tap for each fuse holder was a copper clip tightened down on a small stripped portion of the wire's insulation. The fuse holder was followed by the hinged points of the switches. That was followed by the contact jaws of the switch. The current went out to the loads through one fuse, knife switch and knob and tube wire and came back through a knob and tube wire a knife switch and fuse.
Picture this then. The fuse is the first thing after the bus contact clip. If you want to change it you do it hot at 600 volts. Then the knife of the switch which remains energized when open because of the direction the mechanism faces. So if you wanted to work on a circuit, or perhaps even change a bulb, you could open the knife switch keeping in mind that the knives are always energized on one leg but not the other with no sign of which was which. If you wanted to change the fuse it did no good to open the knife switch unless you wanted more challenges in your life. Opening the double pole knife switch just brought the energized blade close to your fingers when your trying to turn the fuse out of its Edison base screw shell socket.
I'm supposed to figure out why the lobby lights aren't working. Since the service is now 208/120 the AC neutrals are fused. Someone has printed a helpful note on the inside of the panel cover saying caution fused neutrals. I went and found the disconnect for the 3o ampere feeder wires to the field built panel It's a screw shell fused switch from about the 1940s and
actually fully enclosed. It is marked use only slow blow fuse in white wire. I open the switch remove the fuses, lock it closed and off, and go back up the stairs to the panel located above the pie shaped top step. Were was I supposed to clip my safety harness to again?
One of the fuses was blown because the neutral it was installed in was shared with a circuit that supplied the lobby lights. I don a headlamp and open up the box by the front door. I cap of the K&T neutral that has been brought into the box.
I tone out and deenergize the energized conductor from the BX cable.
Replacing the powdered insulation on the GE BX non grounding AC cable's white wire with insulation stripped from a piece of modern wire I carefully put the lighting circuit back together and tie the lighting neutral back into the neutral in the box that had the insulation crumbled off of it. I reenergize the lobby lighting circuit and the muttering amongst the occupants ceases and now I'm a hero.
Back to the ancient panel above the stairs. I shunted out all of the fuse holders and switch poles that are neutrals gauged the wires, Install type S fuse adapters for the wire size of each energized conductor and put in the Type S fuses. Then I close the cabinet that was built by some long dead electrician and say a prayer for him. GO HOME GO HOME.
We didn't have camera phones back then and I no longer have the Polaroid photograph is somewhere in the attic with the rest of my business records.
Tom Horne