Paul Polakoff
Member
I am working on a drilling rig that is fed from a 4160 volt feeder. The transformers on the rig are delta 4160 primaries and wye 600 and 480 secondaries. The manufacturer chose to leave the xo to ground cables off, to allow for a ungrounded system.
My question is safety. The vfd's do not see a ground fault, nor do the breakers.
I have not found NEC to allow it other than for a load that is exclusively a vfd.
Is an ungrounded system safe? Is the potential less allowing the phase to run to the bonded equipment possibly for long periods, verse bonding the xo and having an immediate fault?
Paul Polakoff