Hello,
Please confirm that I'm reading this correctly.
I just looked a an existing pool.
There is a 4 circuit intermatic panel.
There are 2- 240v motor circuits.
One circuit has been tapped off for a 240v ionizer.
I was brought in because they are adding a pool light (low voltage).
So here is my question,
The exterior intermatic panel is fed with thhn, and has an insulated ground.
At the main panel, I see 10-3 nm. (they relocated the pool equipment during a reno).
680.21 (A) (4) mentions a non insulated ground can be used for motors.
Would that 680.21 apply to only motors?
Now that I'm installing a light circuit to the intermatic, would I need to have that panel to have an insulated ground back to the main panel?
I believe so, but would like to make sure.
Also, if I'm right about this, then even adding the ionizer was wrong. Is that correct?
One more thing.
"IF" I was able to take lighting from that panel (proper ground), there is no room for another breaker (120v) so I'm curious to see if I could tap off one off the 240v circs to feed a low voltage transformer. However,
if I'm reading this right, I believe 680.23 (A)(4) voltage limitations prevents me from wiring the low voltage pool lighting transformer to a 240v line circuit. Correct?
Thank You
Please confirm that I'm reading this correctly.
I just looked a an existing pool.
There is a 4 circuit intermatic panel.
There are 2- 240v motor circuits.
One circuit has been tapped off for a 240v ionizer.
I was brought in because they are adding a pool light (low voltage).
So here is my question,
The exterior intermatic panel is fed with thhn, and has an insulated ground.
At the main panel, I see 10-3 nm. (they relocated the pool equipment during a reno).
680.21 (A) (4) mentions a non insulated ground can be used for motors.
Would that 680.21 apply to only motors?
Now that I'm installing a light circuit to the intermatic, would I need to have that panel to have an insulated ground back to the main panel?
I believe so, but would like to make sure.
Also, if I'm right about this, then even adding the ionizer was wrong. Is that correct?
One more thing.
"IF" I was able to take lighting from that panel (proper ground), there is no room for another breaker (120v) so I'm curious to see if I could tap off one off the 240v circs to feed a low voltage transformer. However,
if I'm reading this right, I believe 680.23 (A)(4) voltage limitations prevents me from wiring the low voltage pool lighting transformer to a 240v line circuit. Correct?
Thank You