There are somewhat different rules UL uses for supplemetal fusing of such devices then what the NEC calls for. You may also find wire sizes somewhat smaller inside UL listed assemblies as opposed to premises wiring for the same amperage.Originally posted by chino:
I'm sorry about that, it was my first time to inquire something like this. But anyway what throws me off to double check my doubt is that the VAV unit has the heating element amperage of 15.6 and motor at 1A at 277V. With a total load of 16.6 with a 125%(? Factor) my calculation is telling me to fuse this at 25A with a #10 gauge Cu wire. Am I right? Now if I'm not, is it right for this unit to have a factory installed in-line fuse at 30A?