Called mfgr, no max listed.
Aslo, this is similarly for an exhaust fan. Say an exhaust fan is very small 120V fractional HP, draws say 2A. Per 430.52 table, the largest thermal breaker is 2A X250% = 5A. 5A breaker is not standard so by exception, next standard is 15A. Typically though for exhaust fans in bathrooms, they are on 20A breakers. Is the 20A breaker a violation in this example?
Motors 1 HP or less is a horse of a different color. 430.42(A) or (c), also see 422.10(A)
This is a confusing article.
1. In my example, the exhaust fans are hard wired and I believe this is for only cord and plug connected motors.
2. Upon reviewing this article, it is very confusing. It seems to go in circles. 430.42(C) says 15A branch circuit if overload is omitted per 430.42(A). This then refers you to 430.32(D)(2) for not permanently installed and manually started. Here it has an exception that says it can be on a 20A receptacle? Not following this whole article. Does not make sense, it seems to say you can only plug portable electric tools into a 15A receptacle. Can this bne clarified some? Thanks.
The article does not state it must be cord and plug. 430.32(D) is for overload protection for permanent and non permanent installs. If it is permanent installs then you must use 430.32(B) but again this is for overload protection.
430.32(C) states that if the motor is cord and plug AND individual overcurrent protection is omitted then it must be on a 15 amp circuit. I don't see the contradiction. Most of these motors have overload protection built in.Still not seeing it. Lets say I have a chemical feed pump less than 1 HP that has a noraml 120V plug on the end. It appears that 430.32(D)2 exception is saying I can connect it to a branch circuit protected not over 20A. This looks like I can have a dedicated 20A duplex receptacle on 20A circuit and all is good, maybe even have a switched receptacle. However, looking at 430.42(C), it appears I can only be on a 15A circuit. I am just not seeing it.
Same as aboveHow about a sump pump that gets plugged in? can this only be on a 15A branch circuit?
Because the sections stated are talking about overload protection not the branch circuit size. The size of the branch cir. may be determined by the presence of overload protection.What If I have a thermal switch controlling the receptacle or the motor has integral overload protection. You seem to emphasize overload protection but not sure why.
[/QUOTE]430.32(C) states that if the motor is cord and plug AND individual overcurrent protection is omitted then it must be on a 15 amp circuit. I don't see the contradiction. Most of these motors have overload protection built in.
Same as above
Because the sections stated are talking about overload protection not the branch circuit size. The size of the branch cir. may be determined by the presence of overload protection.
Ok, I think some of this got clarified. Please let me know if I am correct.
Lets say you have 2 small pieces of equipment with a motor in it (like a chemical feed pump), both get plugged into a receptacle, manually started, are assumed non-permenantly installed, are less than 1HP, and both have thermal protection built in. Circuit plans would be a duplex receptacle for each piece of equipment with 20A receptacle and 20A breaker.
Starting with 430.32 per 430.32(D)2 we look to see if it has thermal protection. It does, but it's not required in the equipment as it can be the breaker sized per part IV. Next, we review 430.42 which is applicable because we are dealing with a General-Purpose Branch Circuit. The section is not applicable because we DO have thermal. However, if we didn't, 430.42(c) says we would have to plug into a 15A receptacle but can still have a 20A breaker because of 430.32(2)2 excpeption. Next we move to part IV. Per this section, specifically 430.52, we have to comply with A or D. However, because we have the thermal we do not have to have the breakers sized for 2.5% the motor load hence we can still have the 20A breaker (as opposed to 15 by 450.52(C)). Now comes a trick part, seeing how we have multiple loads on one branch circuit, we have to review 430.53 which is yet more confusion. Because are motors meet the requirements of 430.53(A)1,2, and 3, we can remain with a 20A receptacle and 20A breaker. However, if we have a say a 3/4HP motor that pluggs in, we would need a 15A receptacle and 15A breaker because we exceed the 6 amp load of the first requirement.
I'm not sure if I am right or not, but it is very confusing just to determine the receptacle and breaker size to plug something in. Did I miss the boat someplace?