Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.

No because each heater draws 14.4A, and 28.8A is too much as a continuous load on a 30A breaker. Heating loads are considered continuous so you are limited to 24A (80%) on a 30A breaker. You'll need 2 20A circuits.
 

kwired

Electron manager
Location
NE Nebraska
Can 2 3kw 1ph 208v heaters be installed on 1 circuit? I remember seeing something about 30a max breaker in 424 of NEC.
Correct on the 30 amp - see 424.3. Circuits supplying multiple units are limited to 30 amps, though if it is an infrared heater in other then dwelling, it can be on 50 amp circuit.
 