On AC do they have a power factor? They have iron in them, I don't imaging that they run at unity. Does anyone know?
120127-1135 EST
Yes. Everything has a power factor. This includes when operating on DC. PF ranges from 0 to 1.0 . On DC everything has a PF = 1.0 .
The definition of power factor is Power/VA, and I believe it makes sense to require V and A to be RMS values.
Specifically my Black & Decker 1043-09 reads about 0.94 at 60 Hz with no load, and at nominal speed.
.
120127-2400 EST
An experiment drilling into wood caused the PF to drop to about 0.93. This was not a real high load.
.
The power factor of a universal motor(or any other motor on A.C for that motor) drops with drop in load.120127-2400 EST
An experiment drilling into wood caused the PF to drop to about 0.93. This was not a real high load.
.
But this topic is not about any other motors on AC otherwise you ought to include synchronous condensers.The power factor of a universal motor(or any other motor on A.C for that motor) drops with drop in load.
Not unusual for asynchronous induction motors.One curve I have for a three phase induction motor has a PF of 0.25 at no load, and increasing to a maximum of about 0.9 somewhat above full load, and then slightly drops.
Did anyone claim that it was possible?I've never seen a squirrel cage motor with a PF that improves when you mechanically unload it. How is that even possible?
Did anyone claim that it was possible?
The power factor of a universal motor(or any other motor on A.C for that motor) drops with drop in load.
And PF of squirrel cage induction motors improves as the mechanical load approaches 100% of the motor's capacity.
No problem. Most of us do that from time to time.Sorry, I read this post wrong