N nizak Senior Member Mar 20, 2019 #1 In an application with a multi volt LED driver, does one treat the Common fixture lead as a hot conductor if being wired for 240 volt? Thanks
In an application with a multi volt LED driver, does one treat the Common fixture lead as a hot conductor if being wired for 240 volt? Thanks
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Mar 20, 2019 #2 nizak said: In an application with a multi volt LED driver, does one treat the Common fixture lead as a hot conductor if being wired for 240 volt? Click to expand... Yes; you basically have to ignore the color.
nizak said: In an application with a multi volt LED driver, does one treat the Common fixture lead as a hot conductor if being wired for 240 volt? Click to expand... Yes; you basically have to ignore the color.
N nizak Senior Member Mar 20, 2019 #4 Once a multi volt LED driver is energized at a particular voltage can it be connected to a different voltage and still operate properly? Initial voltage 120, then re energized at 277. Thanks
Once a multi volt LED driver is energized at a particular voltage can it be connected to a different voltage and still operate properly? Initial voltage 120, then re energized at 277. Thanks
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Mar 20, 2019 #5 I've heard of some multi-voltage devices that permanently set themselves to the first voltage applied, but have never encountered one. The manufacturer would be whom you should ask.
I've heard of some multi-voltage devices that permanently set themselves to the first voltage applied, but have never encountered one. The manufacturer would be whom you should ask.