I went to a customer's garage who complained that his GFCI on his work bench wasn't holding, in turn knocking out every outlet tapped off of it. When I inserted my plug tester it read "Hot and Ground reversed". I freed the outlet from the box and tested between the wires (mind you ground is bare): Hot & Ground - 0V; Hot & Neutral - 0V; Ground and Neutral - 120 V.
The customer insisted it was a bad GFCI and of course he was standing over my shoulder. So I changed the GFCI since he paid for it anyway, and of course the problem still existed. I started opening up boxes up the line looking for an incorrect splice. In the panel the neutral and the ground went to the same bar. I found one splice where the wires were pulling taught on the wire nuts and the wire nuts were oversized. However the wires weren't mixed up, hots went to hots and so forth. I opened up the splices and of course they weren't twisted with kliens, just stabbed in. The tips of the copper looked charred a little. I took the reading at this box and they were the same at the GFCI. I got some slack from the romex and went about redoing all 3 splices and used the proper sized wire nut. This fixed the problem! Suddenly all my reading were correct, the plug tester read fine, the GFCI held, and the plug tester tripped it as it should. I'm puzzled as to what problem exactly did I fix?
What splice had to be open to get that hot and ground reversed reading?
The customer insisted it was a bad GFCI and of course he was standing over my shoulder. So I changed the GFCI since he paid for it anyway, and of course the problem still existed. I started opening up boxes up the line looking for an incorrect splice. In the panel the neutral and the ground went to the same bar. I found one splice where the wires were pulling taught on the wire nuts and the wire nuts were oversized. However the wires weren't mixed up, hots went to hots and so forth. I opened up the splices and of course they weren't twisted with kliens, just stabbed in. The tips of the copper looked charred a little. I took the reading at this box and they were the same at the GFCI. I got some slack from the romex and went about redoing all 3 splices and used the proper sized wire nut. This fixed the problem! Suddenly all my reading were correct, the plug tester read fine, the GFCI held, and the plug tester tripped it as it should. I'm puzzled as to what problem exactly did I fix?
What splice had to be open to get that hot and ground reversed reading?