LOTS of opinions on the 50 foot rule for unlisted cables (in my case telecomm cables)
I teach telecomm courses worldwide mainly for the US military and have done so for 20+ years. This is my opinion
The 50 foot limitation can be exceeding if the proper (NEC compliant) conduit system is placed as the raceway in the building. For metallic cables I must use RMC, IMC only. For non-metallic cable (fiber optics with no metallic components such as armor), I can use RMC, IMC, EMT, and PVC. If this practice is acceptable to the AHJ, I'm thinking I'm OK. The key to this is make sure we understand "point of entrance per the NEC.
Your thoughts?
I teach telecomm courses worldwide mainly for the US military and have done so for 20+ years. This is my opinion
The 50 foot limitation can be exceeding if the proper (NEC compliant) conduit system is placed as the raceway in the building. For metallic cables I must use RMC, IMC only. For non-metallic cable (fiber optics with no metallic components such as armor), I can use RMC, IMC, EMT, and PVC. If this practice is acceptable to the AHJ, I'm thinking I'm OK. The key to this is make sure we understand "point of entrance per the NEC.