jimingram
- St Paul MN
In our new state of the art school I noticed that the exterior recessed luminaires have a second lamp in the them. The factory rep. told me that this second halogen lamp is an emergency lamp. The luminaires are 70 watt MH with a 120/277 volt ballast. They operate at 277 volts. The second emergency halogen lamp has a transformer connected to the secondary of the MH ballast. It operates at 120 volt. When the 70 watt MH is on, the halogen is on. Normal operation for these luminaires is dusk to dawn.
These luminaires also have backup power. Backup power is provided by a Liebert battery pack. There are two circuits to these luminares, each coming from a different panelboard. One circuit is from a normal power panelboard and the other is from an emergency panelboard. The two circuits connect to a relay in a lighting control panel. From this relay one conductor goes to the luminaire. This one conductor has either normal or back up power on it. Also of interest, I have observed that the battery power is capable of operating the 70 watt MH lamps.
It seems to me that the second emergency lamp is unnecessary and wasteful. The factory rep. said that these emergency lamps were only suposed to come on with the back up power. This is not so. If there's power on the one conductor, normal or emergency, both lamps are on. Why not remove the emergency lamp? The MH lamp will operate on emergency power.
Your thoughts please.
Jim
Jim