Hi All,
I have a situation where we planned on using general purpose NEMA 4X control stations in a Class I, Div. 1 area so we made them intrinsically safe. The Contractor mistakenly supplied explosion proof (XP) control stations and pushbuttons. They also accidentally combined the IS wiring with non-intrinsically safe.
Given that this is all now XP, I see this as being safe, but it is a violation of NEC Article 504.30. Is it permissible to allow this to slide, or should I have them make revisions and remove the components that make it IS?
Thx,
Jason
I have a situation where we planned on using general purpose NEMA 4X control stations in a Class I, Div. 1 area so we made them intrinsically safe. The Contractor mistakenly supplied explosion proof (XP) control stations and pushbuttons. They also accidentally combined the IS wiring with non-intrinsically safe.