Thank you for taking the time to review this.
I have an unrated Platinum RTD rake probe being inserted into a liquid hydrogen tank. If the probe is welded into the tank, I believe the area above the weld is Class 1 Div2 for 25ft sphere.
If the probe is flange mounted to the tank, I believe the area around the flange is Class 1 Div 1 for a 3ft sphere.
As I understand, the RTDs would require an wiring method consistent with C1D1 such as IS Barrier, Armored Cable, Conduit and seal offs, mineral insulated...
If we are meeting C1D2 with unrated RTDs, can I install the same PLTC cable with rated glands etc. the same as we would use with other instrumentation or do I still need to use the C1D1 installation methods (most likely IS Barriers) since the RTDs are not rated for hazardous locations?
Any thoughts would be greatly appreciated.