Will Wire
Senior Member
- Location
- California: NEC 2020
- Occupation
- Electrical Contractor
Problem: Customer's original bottom fed G.E. 100-amp meter/distribution panel was converted to a sub panel without isolating the grounded conductors from the equipment grounding conductors. The panel is being fed through the bottom meter and neutral lugs, on the Utility side that are now jumped to the top meter lugs connected to the 100-amp main. Plastic meter cover in place. The sub panel is about 8" from the new 200-amp service.
My understanding is that this is not right or safe at all. Because of NEC 250.24(A)(5) in the very least the grounded conductors should be on an isolated and insulated buss bar, separate from any equipment grounding conductors, or any non-current carrying parts.
If the grounded conductors are isolated on an insulated Neutral buss bar, will that be an acceptable fix? Are there other Code violations?
Thanks, Trent
California: NEC 2020 Edition
My understanding is that this is not right or safe at all. Because of NEC 250.24(A)(5) in the very least the grounded conductors should be on an isolated and insulated buss bar, separate from any equipment grounding conductors, or any non-current carrying parts.
If the grounded conductors are isolated on an insulated Neutral buss bar, will that be an acceptable fix? Are there other Code violations?
Thanks, Trent
California: NEC 2020 Edition