Unserground URD splice

Status
Not open for further replies.

speedystevie

Senior Member
Location
Long Island, NY
On a job I am working on a back-hoe operator managed to make a clean cut on a underground URD run. The URD is 4/0 and is fused @ 100Amps. The run is used to power lighting on a tennis court about 300' away from the house.

Is there a such thing as an underground splice kit for such a problem.

Or will I be forced to have two splice boxes to fix the problem.

Any words of wisdom would be helpful, thank you
 
Re: Unserground URD splice

Yes, ther are products specifically designed for this purpose and are widely available. The use of boxes are not required per 300.5(E).
 