I know its in there somewhere,,,,,where does it say you can slack loop cable 6 feet,,,,,,ie: jumping from one cable tray to another?

dick
 

jumper

Senior Member
Are you talking about this:

392.6 Installation.
(A) Complete System....

Where cable trays support individual conductors and
where the conductors pass from one cable tray to another,
or from a cable tray to raceway(s) or from a cable tray to
equipment where the conductors are terminated, the distance
between cable trays or between the cable tray and the
raceway(s) or the equipment shall not exceed 1.8 m (6 ft).
The conductors shall be secured to the cable tray(s) at the
transition, and they shall be protected, by guarding or by
location, from physical damage.
 

dicklaxt

Senior Member
Didn't know you had posted and no you are not wrong and yes I guess I answered my own question too,is there something wrong with that.I guess I could have let it ride but saw no reason to.