bryonb
- Oklahoma City, OK
Please forgive me if this has been discussed before. I did a search of the forums, but couldn't locate this topic.
What is the general consensus as to the deletion of 3XX.30(C) Unsupported Raceways section in the IMC, RMC, PVC, RTRC, and EMT articles? The original proposal 8-24a clearly states that the intent of the proposal was to clarify that additional support is not needed for sections of conduit shorter than 36". By the way, the proposal was submitted by James W. Carpenter, IAEI, who is also the Chairman of the Technical Correlating Committee. The proposal was accepted with a panel statement of "CMP-8 does not necessarily agree with the submitter's Substantiation. Securement requirements are found in 342.30(A)". However, part of the panels statement in ROC 8-10 states "..."additionally, the raceway terminations are to terminate the raceway, not to provide support..." and "...Any decision to omit the support required by general rule with 3' of raceway terminations is a decision best made in the field by the AHJ based on the circumstances of the given installation...".
In the book ?Significant Changes to the NEC 2001 published by the NJATC and NECA, it summarizes the change stating ?An 18-inch or smaller nipple will now require a means of securement?. However, the book ?NEC 2011 Analysis of Changes" published by the IAEI and NFPA states ?Short racesays (18? to 36?) no longer require additional support?.
I?m of the opinion that additional support isn?t needed for short sections of raceways, but there seems to be conflicting opinions on this issue (yet again) and the statements of the CMP seem to be contributing to the confusion.