Let me be honest, I have tried to be a study of the NEC (2008), but it vexes me.
Recently, I attempted to follow the mind(s) of an electrical contractor and an engineer, but have failed. Please humor my description of what I see.
There is a MCC breaker feeding 2 sets of 3 phase 480v 350 MCM conductors to a trough. The MCC breaker is set for 300 amp trip rating. The conductors, which I can tell, are rated (ampacity) for more than the breaker. And as far as I can tell, no conductors have been "upsized" for any electrical reason. So far so good?
Here's what is from the trough. there are 3 fused disconnects, the first disco has a set of phase conductors and a grounding conductor, the second disconnect is fed from the second set of MCC phase conductors, with ground, but has an extra set of lugs on the line side, so the third disconnect is fed from the second disco line side, lug to lug, with 350 MCM. Kind of like an MLO panel. So, are the disco "feeds" a feeder? I think so. With that thought in mind, the load(s) following the fused disconnects are branch circuits.
Also, when the NEC describes that all conductors must be in the same raceway, how is that determined? I see two complete sets of conductors, one set feeding disconnect one and two, even though they originate ona single breaker, and are common to the trough, but there is a phase ABC and ground for each downstream disconnect. Mind there is a combination of rigid and IMC for raceways.
So, if I am reading this right, there are no tap conductors, seeing how the MCC breaker is set lower than the ampacity of the conductors. There are no concerns for separating a set of the 3 phase conductors from the trough, seeing as how that circuit's conductors are in a single raceway and finally, once the disconnect fuses enter the fray,the conductors from that point are protected by the fuses (ocpd).
I am seeking enlightment to affirm or negate my limited knowledge. Forgive my poor explanation of what I attempt to describe.
What seems to be at issue is the idea that the MCC to trough conductors are or are not taps.
Feel free to question me or my poor description, thanks in advance,
D.
Recently, I attempted to follow the mind(s) of an electrical contractor and an engineer, but have failed. Please humor my description of what I see.
There is a MCC breaker feeding 2 sets of 3 phase 480v 350 MCM conductors to a trough. The MCC breaker is set for 300 amp trip rating. The conductors, which I can tell, are rated (ampacity) for more than the breaker. And as far as I can tell, no conductors have been "upsized" for any electrical reason. So far so good?
Here's what is from the trough. there are 3 fused disconnects, the first disco has a set of phase conductors and a grounding conductor, the second disconnect is fed from the second set of MCC phase conductors, with ground, but has an extra set of lugs on the line side, so the third disconnect is fed from the second disco line side, lug to lug, with 350 MCM. Kind of like an MLO panel. So, are the disco "feeds" a feeder? I think so. With that thought in mind, the load(s) following the fused disconnects are branch circuits.
Also, when the NEC describes that all conductors must be in the same raceway, how is that determined? I see two complete sets of conductors, one set feeding disconnect one and two, even though they originate ona single breaker, and are common to the trough, but there is a phase ABC and ground for each downstream disconnect. Mind there is a combination of rigid and IMC for raceways.
So, if I am reading this right, there are no tap conductors, seeing how the MCC breaker is set lower than the ampacity of the conductors. There are no concerns for separating a set of the 3 phase conductors from the trough, seeing as how that circuit's conductors are in a single raceway and finally, once the disconnect fuses enter the fray,the conductors from that point are protected by the fuses (ocpd).
I am seeking enlightment to affirm or negate my limited knowledge. Forgive my poor explanation of what I attempt to describe.
What seems to be at issue is the idea that the MCC to trough conductors are or are not taps.
Feel free to question me or my poor description, thanks in advance,
D.