Probably so.Yes but that would be mean it would have to be driven down eight feet
I think water piping has it's own section because they were once part of a fairly large network of piping and were likely to have multiple connections to electrical grid as well, meaning possibly pretty low impedance earthing connection when compared to some other more limited underground piping systems."A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductor(s) or jumper(s), if installed."
I don't see anything in that language that implies it must be in use. It's still a water pipe isn't it?
"A metal underground water pipe in direct contact with the earth for 3.0 m (10 ft) or more (including any metal well casing bonded to the pipe) and electrically continuous (or made electrically continuous by bonding around insulating joints or insulating pipe) to the points of connection of the grounding electrode conductor and the bonding conductor(s) or jumper(s), if installed."
I don't see anything in that language that implies it must be in use. It's still a water pipe isn't it?
I agree, it's just a piece of metal in the ground that doesn't qualify as an electrode.If there isn't any water in it then it is not a water pipe, IMO.