Hello,
I've recently been asked to install an new panel fed from an existing 240V Delta service. While metering the service, I encountered some unusual results:
A-N = 121V
B-N = 218V
C-N = 122V
A-B = 121V
A-C = 243V
B-C = 119V
The phase-neutral readings appear normal for a Delta service, however the ~120V measurement between phase A-B and B-C seem unusual... my understanding with 240V Delta services whether "open" or "closed" is that voltage between any two phases should be 240V.
Does this sound like it could be an issue with the utility, or perhaps some unusual transformer configuration on the pole which is actually intended to yield 120V between A-B and B-C that I've not encountered before?
Thanks!