Unusual amp reading on secondary of transformer

Status
Not open for further replies.

naplespete57

Member
Location
Eastern Kentucky
Occupation
Project Manager in Conveyor Industry
Just installed a delta delta transformer. When I ran the motor it is designed for I got the following readings.. Phase A 11.4 Phase B 14.1 Phase C 11.4.

Why the different reading? What should I check? Transformers only purpose is to run motor, nothing else is tapped out of it.

Is it a matter of concern?

Thanks!
 
AS noted above and.

Check primary unloaded/loaded.

Check secondary unloaded/loaded.

Check transformer taps.

Other factors orientation of amp clamp, check all connections, if possible measure resistance from secondary terminal to motor for voltage drop across conductors, do same for primary side from service to primary connections.

Possible motor winding issues (I have had motors in the past with this issue we (and others) did every test under the sun and found nothing.
 