Thank you for the reply. It is for a Cutler Hammer panel. I ordered a 2-pole 60 amp breaker and this is what they sent. It is a 2-pole breaker, but it has 30 amps on one pole and 60 on the other. The only use I can think of would be for something that needs 2 different 120 volt loads that would share a neutral. Something like a machine with two different size motors.It would help if we saw the configuration of the back, but the tan handle suggests that it could be a Cutler-Hammer classic circuit breaker.
I agree.But I'm leaning toward 'oopsie' on the unmatched pole rating numbers.
Those both have the same size lugs, so my guess is that the breakers are of the same rating, but one just has the wrong handle.
Unless it’s supplying two 120V loads, one on a 30A circuit and the other on a 60A. But I don’t think I’ve ever seen a 120V, 60A load.Well if one side is actually 30A and given the fact it's common trip it would never carry a 60 amp load period.![]()
In that case there's no reason for a two pole breaker.Unless it’s supplying two 120V loads, one on a 30A circuit and the other on a 60A. But I don’t think I’ve ever seen a 120V, 60A load.