jeff48356
Senior Member
- Location
- Livonia, Michigan
Have any of you ever discovered unusual (or dangerous) electrical situations when doing a service upgrade at someone's house? Here's TWO for the record book, on a job I did today in my neighborhood. The old panel was a Pushmatic, probably installed in the 70's. The original panel was actually fuses from when the house was built in 1962.
The first thing I discovered was that the meter cable (#2 SEU) was the original, so it was already in bad shape outdoors. But the idiot who installed the Pushmatic, rather than replacing the meter cable, spliced three conductors OUTSIDE of the panel using split-bolts and friction tape to extend those from the original SEU because they must have been too short to reach the lugs. Easy fix since I replaced the meter cable as should have been done before. The second thing was that the guy who lives there now had wired a 240V electric dryer using a 30A breaker on #12 copper-clad cable! That crap is only supposed to be good for 15A if I'm not mistaken.
So my question to you is, what would you do if you run into situation #2? Would you reconnect the dryer using a 15A 2-pole breaker (which would probably trip frequently) or would you rewire the circuit using #10-3 Romex? If the latter, how would you go about adding an appropriate cost onto the bill, especially considering the price of Romex these days?
The first thing I discovered was that the meter cable (#2 SEU) was the original, so it was already in bad shape outdoors. But the idiot who installed the Pushmatic, rather than replacing the meter cable, spliced three conductors OUTSIDE of the panel using split-bolts and friction tape to extend those from the original SEU because they must have been too short to reach the lugs. Easy fix since I replaced the meter cable as should have been done before. The second thing was that the guy who lives there now had wired a 240V electric dryer using a 30A breaker on #12 copper-clad cable! That crap is only supposed to be good for 15A if I'm not mistaken.
So my question to you is, what would you do if you run into situation #2? Would you reconnect the dryer using a 15A 2-pole breaker (which would probably trip frequently) or would you rewire the circuit using #10-3 Romex? If the latter, how would you go about adding an appropriate cost onto the bill, especially considering the price of Romex these days?