1. The NEMA Bulletin " The Thermal Effects of Residential Installed Type NM-B Encased in Spray Insulation " is in the process of being pulled.
2. Goodson Engineering Publication " Effects of Polyurethane Foam Systems on Wiring Ampacity " raises serious questions of ampacity in NM-B cables in Spray Foam. This was brought before the CMP, which I was told was the reason they are asking for a comprehensive study. Such a study apparently does not exsists, at this time on spray foam insulation.
3. A qualitative definition of "Spacing" with reguard to NM-B cable is not coming in the next code cycle I was told, because no one wants to define it at this time.
4. Because the "R" factor of spray foam increases with depth, the depth of the spray foam will probably increase the temperatures of conductors.
5. Older Houses that have heavily loaded circuits and in all probably NM-B cable not spaced, spray foamed could pose a problem.
2. Goodson Engineering Publication " Effects of Polyurethane Foam Systems on Wiring Ampacity " raises serious questions of ampacity in NM-B cables in Spray Foam. This was brought before the CMP, which I was told was the reason they are asking for a comprehensive study. Such a study apparently does not exsists, at this time on spray foam insulation.
3. A qualitative definition of "Spacing" with reguard to NM-B cable is not coming in the next code cycle I was told, because no one wants to define it at this time.
4. Because the "R" factor of spray foam increases with depth, the depth of the spray foam will probably increase the temperatures of conductors.
5. Older Houses that have heavily loaded circuits and in all probably NM-B cable not spaced, spray foamed could pose a problem.