My blood pressure just went up 35%, Tom, thanks. :D

Section 250.53(A):
CMP-5 accepted a proposal to require any single rod, pipe, or plate electrode to be supplemented by one additional electrode with an exception that demonstrates that the single electrode has a resistance not exceeding 25 ohms to ground.

Stupid! Stupid! Stupid! :mad:
 

electricalperson

Senior Member
Location
massachusetts
*New* 404.2(C):
This requires lighting loads supplied by grounded general purpose circuit to have a grounded (neutral) circuit conductor at the switch outlet locations.

they mentioned that was one of the proposals for the 2008 code at the super code conference in 2007
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
My blood pressure just went up 35%, Tom, thanks. :D

Quote:
Section 250.53(A):
CMP-5 accepted a proposal to require any single rod, pipe, or plate electrode to be supplemented by one additional electrode with an exception that demonstrates that the single electrode has a resistance not exceeding 25 ohms to ground.



Stupid! Stupid! Stupid! :mad:


George does this really change much?
 