A heat pump replacement caused the need to replace an existing 20A breaker + #12 wire with a 30A breaker +#10 wire. The new #10 wire is NM-B. The original #12 wire was UF-B.
From the circuit breaker the wire is routed thru a conduit to below grade. The wire makes approx. 90 deg bend into the dirt for 12-18" then passes thru a hole drilled into the brick foundation. Under the house (dark dry place where no one wants to go - approx 24" height), the wire is routed approx 24" barely covered with dirt (assumed to pass by the crawl space opening without getting snagged when one crawls in) and then another 36" on top of dirt to a conduit exiting the brick foundation to the outside heat pump unit.
If I've read the NEC correctly on the use of NM type wire, it should be ok. The only concern is the 12-18" in the dirt. Can NM be used in this installation?
From the circuit breaker the wire is routed thru a conduit to below grade. The wire makes approx. 90 deg bend into the dirt for 12-18" then passes thru a hole drilled into the brick foundation. Under the house (dark dry place where no one wants to go - approx 24" height), the wire is routed approx 24" barely covered with dirt (assumed to pass by the crawl space opening without getting snagged when one crawls in) and then another 36" on top of dirt to a conduit exiting the brick foundation to the outside heat pump unit.