Upgrade on remodel

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Locally it has always been a policy that on remodel work if the wall/ceiling cover were removed that portion of the structure had to be brought up to current codes.
Is that policy actually in writing in any National codes such as IRC ???
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Here, if you renovate 50% or more of the total area, the entire structure must be brought current.

It may be one of those rules that local jurisdictions individually adopt.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
That "policy" has been in effect in this and surrounding areas for years and, so far, the source is elusive.
 

david

Senior Member
Location
Pennsylvania
International residential code was mentioned

A lot of states have adopted the international existing building code that's where you'll find the percent

Sent from my SM-S901U using Tapatalk
 

Earthed

Member
Location
Ohio
Occupation
Electrical Inspector, Plumbing Inspector, Residential Building Official
Existing buildings. From Ohio which is IRC based.

113.4 Additions and Alterations


Additions or alterations to residential buildings shall conform with the requirements of the code for new construction and shall be approved by the residential building official. Additions or alterations shall not be made to an existing residential building or structure which will cause the existing residential building or structure to be in violation of any provisions of this code. Portions of the structure not altered and not affected by the alteration are not required to comply with the code requirements for a new structure.

Exception: For residential buildings and structures in flood hazard areas, any additions, alterations or repairs that constitute substantial improvement of the existing structure, shall comply with the flood design requirements for new construction and all aspects of the existing structure shall be brought into compliance with the requirements for new construction for flood design.
Share url icon



Open options


113.5 Replacement of Systems, Components and Materials


Replacements of an existing system (egress, fire protection, mechanical, plumbing, etc.) and materials or building components not otherwise provided for in this section, shall conform to that required for new construction to the extent of the alteration. The existing systems, materials, or components shall not be required to comply with all of the requirements of this code for new construction except to the extent that they are affected by the alteration. Replacement of existing systems, materials, or components shall not cause them to become unsafe, hazardous, overloaded, or become less effective than when originally installed, constructed, and/or approved.
 