We are looking at that a project that currently has an ungrounded Center-Tapped Delta service entrance to provide 120/240V/208V service to a facility to feed 120V single phase loads and 240V 3-Phase loads (not sure how many actual 208V loads if there are even any). There are also have 480V 3-Phase loads that are fed via step-up transformers to 3-Phase panels.
The customer is now upgrading their service entrance to a 480V wye-grounded secondary which will now feed the 480V loads directly. For the existing 120/240V loads we will need to install (2) 500kVA delta center-tapped transformers to connect to the existing 120/240V panels in order to continue to feed the existing 120V 1-Phase loads and 240V 3-Phase loads.
I had initially thought about perhaps converting this the 120/240V loads over to a more traditional 120/208V however they are several motors that are only rated for 240V that could perhaps be negatively impacted from operating at lower voltage. There are some motors that have a 208-240V rating however there appear to just be too many listed specifically for 240V to justify changing to 120208V system.
I was curious to hear thoughts from others weather the change to a 120/208V system should be further investigated or given the number of existing motors and plant personnel's familiarity with the existing system to just leave it as a 120/240V system?
Any things that need to be considered with providing the new center-tapped transformers to re-feed existing 120/240V panels?
The customer is now upgrading their service entrance to a 480V wye-grounded secondary which will now feed the 480V loads directly. For the existing 120/240V loads we will need to install (2) 500kVA delta center-tapped transformers to connect to the existing 120/240V panels in order to continue to feed the existing 120V 1-Phase loads and 240V 3-Phase loads.
I had initially thought about perhaps converting this the 120/240V loads over to a more traditional 120/208V however they are several motors that are only rated for 240V that could perhaps be negatively impacted from operating at lower voltage. There are some motors that have a 208-240V rating however there appear to just be too many listed specifically for 240V to justify changing to 120208V system.
I was curious to hear thoughts from others weather the change to a 120/208V system should be further investigated or given the number of existing motors and plant personnel's familiarity with the existing system to just leave it as a 120/240V system?
Any things that need to be considered with providing the new center-tapped transformers to re-feed existing 120/240V panels?