Here's the situation:
An existing apartment building is fed as follows
Main service is fed from a pole mounted 120/240V 50KVA utility transformer single-phase
The service is tapped by two 400A disconnects each feeding a meter bank consisting of 19 meters - each one rated for
120/240V single phase
Part of the basement is being renvoated for 8 new apartments. The demand for which need to be calculated per NEC.
The new service can't be sized with the existing demand becasue you can't get the demand for residential meters so we have
to size the existing per NEC.
The total demand calcualted per NEC is too large for a sinle-phase service so we have to size the service for 120/208V
3-phase and back feed the 400A disconnects for 120/208V single-phase...which should not be a big deal.
We are going to call for a new 800A tap box with a new meter bank consisting of 8 meters and for the existing 400A feeders
to be extended and connected into the new tap (located within 25ft of the existing disconnects).
We looked into bringing in a serperate service but adding a fire wall was an issue.
I was just wondering - with the information given above - what others on here have done or would do for this type of
situation...looking forward to your replies.
An existing apartment building is fed as follows
Main service is fed from a pole mounted 120/240V 50KVA utility transformer single-phase
The service is tapped by two 400A disconnects each feeding a meter bank consisting of 19 meters - each one rated for
120/240V single phase
Part of the basement is being renvoated for 8 new apartments. The demand for which need to be calculated per NEC.
The new service can't be sized with the existing demand becasue you can't get the demand for residential meters so we have
to size the existing per NEC.
The total demand calcualted per NEC is too large for a sinle-phase service so we have to size the service for 120/208V
3-phase and back feed the 400A disconnects for 120/208V single-phase...which should not be a big deal.
We are going to call for a new 800A tap box with a new meter bank consisting of 8 meters and for the existing 400A feeders
to be extended and connected into the new tap (located within 25ft of the existing disconnects).
We looked into bringing in a serperate service but adding a fire wall was an issue.
I was just wondering - with the information given above - what others on here have done or would do for this type of
situation...looking forward to your replies.