Working on an existing generator inlet box for a 30A generator connection. The wire is currently #8 thhn/thwn-2 CU in sch 40 PVC conduit. This was sized based on NEC table 310.16 60 deg. column since the load was under 100A (it was upsized from #10 to #8 to insure adequate voltage). The inlet box is being upgraded to a 50A genset connection. With that said, the currently installed wire is good for 50A under the 75-degree column. Since the conection is under 100A, is it acceptable to use the 75 degree column and the installed wire at 50A if both the breaker and the plug terminals are rated for 75 degrees? Or is there any other determining factors before I can use the 75 degree column? The conductor is southwire simpull e51583 with insulation rated for 75 degrees when used as THWN or 90 degrees when used as THWN-2 (no oil).