Hey everybody, just wanted to ask for your thoughts on a work situation.
During a recent emergency at work, a member of upper management at our facility asked 4 of my electricians to hook up a 480 volt 6KW portable electric heater to the motor junction box(aka peckerhead) of one of the station dry pit submersible pumps. :happysad:
The pump motor is 3 phase/460/135hp/101kw. There are 4 of them in the station. Each is controlled by its own VFD in the MCC on the upper level. The motors are rated class 1 div 1 and are located in the drywell of the station. Each is fed by a parallel pair of extra hard usage SO cable, made by the manufacturer.
The station had been flooded and at this point he wanted to get the portable heater energized to start drying out the moisture in the motors and their cables. Meantime, a contractor was still working in the room, pressure washing the sludge off of the walls.
my guys said "no", it's a code violation and very unsafe. The next day I had a pretty charged conversation with him explaining how wrong he was to ask them to do that, they weren't being insubordinate or incompetent, on the other hand they were being professional. I said I would have told him the exact same thing if he asked me to do that.
Now...he has challenged me to explain what NEC code violations could there have been if the guys did what he told them to do.
So my question to you is just the same, what code articles would you say would have a bearing on my boss's boss's boss's installation of a portable heater cable in the peckerhead of a hazardous location motor which is fed from a VFD? LOL
here is what I have come up with so far:
110.12
110.27
110.31(B)(1)
210.20A
240.5(B)(1)
240.21
424.93
this only took about 15 mins, I haven't even really started with 430 yet
430.62A
430.24
thanks guys,
Mr. Rogers
During a recent emergency at work, a member of upper management at our facility asked 4 of my electricians to hook up a 480 volt 6KW portable electric heater to the motor junction box(aka peckerhead) of one of the station dry pit submersible pumps. :happysad:
The pump motor is 3 phase/460/135hp/101kw. There are 4 of them in the station. Each is controlled by its own VFD in the MCC on the upper level. The motors are rated class 1 div 1 and are located in the drywell of the station. Each is fed by a parallel pair of extra hard usage SO cable, made by the manufacturer.
The station had been flooded and at this point he wanted to get the portable heater energized to start drying out the moisture in the motors and their cables. Meantime, a contractor was still working in the room, pressure washing the sludge off of the walls.
my guys said "no", it's a code violation and very unsafe. The next day I had a pretty charged conversation with him explaining how wrong he was to ask them to do that, they weren't being insubordinate or incompetent, on the other hand they were being professional. I said I would have told him the exact same thing if he asked me to do that.
Now...he has challenged me to explain what NEC code violations could there have been if the guys did what he told them to do.
So my question to you is just the same, what code articles would you say would have a bearing on my boss's boss's boss's installation of a portable heater cable in the peckerhead of a hazardous location motor which is fed from a VFD? LOL
here is what I have come up with so far:
110.12
110.27
110.31(B)(1)
210.20A
240.5(B)(1)
240.21
424.93
this only took about 15 mins, I haven't even really started with 430 yet
430.62A
430.24
thanks guys,
Mr. Rogers