chris_carlson
New member
- chesapeake, va
I am trying to find out proper information on bonding of a ups system.
The normal feed has a 4 wire (3 phase, ground) input to the 160 kVA UPS. The AC is converted to DC, and back to AC through the inverters, while charging the battery circuit (trickle charge). The output has a 5 wire (3 phase, neutral, ground). The UPS has a bypass feed input which has 5 wires (3 phases, a neutral {bonded to ground at the input transformer approximately 75 to 100 feet away}, and ground) input. That same neutral is directly connected to the load neutral and UPS output neutral. While in normal operating conditions the normal feed has a balanced current draw on the 3 input phases of about 80 amps each. The bypass 3 phases inputs have no current but the neutral bypass current is about 14 amps. The two feeds have grounding straps connected the conduit to the ground. The normal feed conduit straps have less than 1 amp of current. The Bypass conduit straps have about 3 amps of current.
Some of the specific questions I have are:
1) With a 3 phase input and a 3 phase, neutral output, is the UPS a separately derived service?
2) If so then I am assuming that the UPS output neutral should be grounded at the UPS output?
3) And If so how do I separate the bypass neutral from the output of the UPS and the load neutral?
4) Would an isolation transformer or a neutral overlapping 4 pole switch be better to isolate the neutrals?