I'm working on a 24 VDC UPS, 1600 Amp Hour, 75Amp system.
I'm trying to find out what type of cable I need to be using.
There will be 5 trays of batteries and each tray will have a maximum current draw of 15 Amps. Each tray will be fused at 20Amps. Each tray will have 4, 100 Amp VLRA batteries.
The wiring from the UPS to the Fire Panel will be a single pair, with a maximum current of 75 Amps and will be fused at 100 Amps.
I intend to size the cable for each tray to handle 25 Amps min., and from the UPS to the Fire Panel, for 125 Amps min.
I've looked at article 700, 701, and 702 for some hints on the type of cable but can't seem to find any.
Anybody experience with UPS's and the types of cables?
Do you see anything wrong with the logic on how I intend to size the cables?
Regards
I'm trying to find out what type of cable I need to be using.
There will be 5 trays of batteries and each tray will have a maximum current draw of 15 Amps. Each tray will be fused at 20Amps. Each tray will have 4, 100 Amp VLRA batteries.
The wiring from the UPS to the Fire Panel will be a single pair, with a maximum current of 75 Amps and will be fused at 100 Amps.
I intend to size the cable for each tray to handle 25 Amps min., and from the UPS to the Fire Panel, for 125 Amps min.
I've looked at article 700, 701, and 702 for some hints on the type of cable but can't seem to find any.
Anybody experience with UPS's and the types of cables?
Do you see anything wrong with the logic on how I intend to size the cables?