WECC
New member
- Location
- Charlotte ,NC
We have a small regional 911 call center that also handles state police and EMS commuications networks. There is no alternate site to transfer these systems to at this time for a shutdown.
They are powering the communications equipment through a single phase 208V 16KVA UPS system that is having problems and needs to be replaced. The UPS was not provided with an external bypass but has an internal bypass that takes normal power around the inverter and batteries and sends it through an isolation transformer before it feeds the panel.
The owner has purchased an identical UPS unit to the one that is failing and needs to change it out without an outage. We believe we can take the new UPS place it in bypass and use it to parralell feed the equipment panel then shut down the old ups and remove it from the system.
Basically we will be feeding the same panel with (2) Isolation transformers built into the UPS units for a short period of time while the old one is removed. We beleive it will work as long as we keep the phasing correct and check for voltages between the 2 feeds before energizing the new unit.
If anyone has some thoughts we would like to hear them.
They are powering the communications equipment through a single phase 208V 16KVA UPS system that is having problems and needs to be replaced. The UPS was not provided with an external bypass but has an internal bypass that takes normal power around the inverter and batteries and sends it through an isolation transformer before it feeds the panel.
The owner has purchased an identical UPS unit to the one that is failing and needs to change it out without an outage. We believe we can take the new UPS place it in bypass and use it to parralell feed the equipment panel then shut down the old ups and remove it from the system.
Basically we will be feeding the same panel with (2) Isolation transformers built into the UPS units for a short period of time while the old one is removed. We beleive it will work as long as we keep the phasing correct and check for voltages between the 2 feeds before energizing the new unit.
If anyone has some thoughts we would like to hear them.