I'm looking for any good ideas, and to ask a few questions about an upcoming project.
An outside contractor is installing a new UPS in our IT room, I need to run a feeder from a closet off the side of the room (from an I-line panel 480V 3 phase) to the UPS 100' away as the crow flies. Then a second feeder back from the UPS to the closet again to feed the UPS panel in the closet.
I'm told the feed will be a 150 amp breaker, so I am running 1/0 conductors. We'll run 1 1/'2" conduit.
My questions:
An outside contractor is installing a new UPS in our IT room, I need to run a feeder from a closet off the side of the room (from an I-line panel 480V 3 phase) to the UPS 100' away as the crow flies. Then a second feeder back from the UPS to the closet again to feed the UPS panel in the closet.
I'm told the feed will be a 150 amp breaker, so I am running 1/0 conductors. We'll run 1 1/'2" conduit.
My questions:
- Are there any better/faster/cheaper options than running EMT conduit under the raised floor in the room. M/C cable? FMC?
- The floor is full in some spots, is there a pre-made conduit/cable stand that would make installation easier/faster? In my mind, installing above all the cables and conduits already laying in the bottom of the floor.