Hi all,
I had a discussion with the CTO from the company I work at the other day regarding the amount of power a UPS consumes. We have this scenario: the load is 364kVA so I naturally put in my design plans a 400kVA UPS to feed this load. The UPS itself is being fed by a switchboard, and my conclusion is that this switchboard sees a load of 400kVA (the UPS and its batteries) and we consider 10% for battery recharge, so the total load would 440kVA. The switchboard doesn't care or know how much the final load is, it just sees a UPS to be energized. The CTO states that the total load is 364kVA plus the 10% = 364*1.1 = 400.4kVA.
Which one of us is right?
Thanks.
I had a discussion with the CTO from the company I work at the other day regarding the amount of power a UPS consumes. We have this scenario: the load is 364kVA so I naturally put in my design plans a 400kVA UPS to feed this load. The UPS itself is being fed by a switchboard, and my conclusion is that this switchboard sees a load of 400kVA (the UPS and its batteries) and we consider 10% for battery recharge, so the total load would 440kVA. The switchboard doesn't care or know how much the final load is, it just sees a UPS to be energized. The CTO states that the total load is 364kVA plus the 10% = 364*1.1 = 400.4kVA.