I would suggest to bring 4W + ground to the UPS. Some smaller UPSs are not "online" type, and essentially pass power through until a power quality issue is detected. If 120V is available on the output, it is likely that you need a neutral on the input.
Granted some better UPS's do have some isolation from input to output and might not need a neutral on the input, but better to wire nut it off if you don't need it, than not have it.
Did they tell you the 90A CB? If you sized it be sure you are giving capacity headroom for full load plus losses and battery recharge.