On the drawing
On the drawing
On the drawing:
The UPS input, at the rectifier, is a single source feed from breaker (E) 2ERA downstream of the 45 kva xfmr.
The bypass input is a single source feed from the 2PDP switchboard.
It looks like when the UPS is online it is loaded on the 2ERA breaker only but when it goes to bypass, the bypass loads on the 2PDP switchboard. That's not really dual source unless you count the ATS and genset upstream of the 45 kva xfmr.
Looking at the drawing the bypass feeder from 2PDP is 3 #1 and 1 #6 gnd so that's 3 ph 3 wire no neutral. The feeder from 2ERA is 4 #1 and 1 #6 gnd, 3 ph 4 wire.
So my first question is, with the UPS in bypass supplying 3 ph 4 wire loads, where does the neutral load current circulate to if the neutral does not come in with the bypass feed from 2PDP. The UPS may have a filter transformer section at the inverter output, that transformer would be delta in from the inverter and Y out, separately derived and grounded, to the loads. If so, no neutral at the input is OK, if not, not OK.
The rectifier source transformer should be solidly grounded and earthed Y. That could be checked and if so, the neutral source reference to the UPS should be good, immune to ATS switching.
If as the drawing shows the bypass feeder from 2PDP is 3 wire no neutral, then the UPS has only one neutral coming to it from one separately derived source, no alternate shunt path to ground for neutral current.
Still unclear, I would check:
1. Is there no neutral from 2PDP as the drawing shows.
2. Does the UPS output have an output (inverter) filter transformer that is delta to Y and separately derived, grounded and earthed.
3. If #2 is no and #1 is yes, if in UPS bypass mode does the load neutral current improperly circulate through 2ERA instead of 2PDP which carries the load in bypass.
4. I'm still assuming the rectifier load is delta and the input neutral is only used for sensing and control circuitry. However the neutral circuit external to the UPS could still be an issue, either two separate line side neutrals coming together (2ERA and 2PDP) or load side neutral current flowing to the wrong place in bypass mode.