Looking for a little help. Need to provide 12 hour back up at full load for several pieces of equipment. This equip is plugged into 20a receptacles. How would I get calculated full load? Based on equip cut sheets I'm assuming....what do I look at and what's the formula? Thanks
 

mgookin

Senior Member
Location
Fort Myers, FL
Looking for a little help. Need to provide 12 hour back up at full load for several pieces of equipment. This equip is plugged into 20a receptacles. How would I get calculated full load? Based on equip cut sheets I'm assuming....what do I look at and what's the formula? Thanks

Can you give us the equipment schedule?
 

Ingenieur

Senior Member
Location
Earth
Is a single 20 ckt?
amp clamp it
120 x A = kva
I'ld bump it up 25% or next std rating

you need ~ A x 1hr ~ A-hrs at 120 vac
the UPS data sheet wil usually give % output for various time periods

you will need a decent size batt pack
12 hrs is a long time
hardwired or plug in?
 

dfmischler

Senior Member
Location
Western NY
Occupation
Facilities Manager
Customers say that they want a UPS that will carry the load for an extended period without a generator. But what they really want is a magic box that will make electricity for 12 hours without any maintenance, and without any concern for back-to-back outages.

It was explained to me many years ago that it is usually a mistake to configure a UPS to handle an extended outage without a generator. You wind up with a big expensive bank of batteries that will need to wait for utility power to be restored before they can be recharged. You simply can't handle another outage right after recovery of utility power because the batteries haven't been able to recharge. The big, noisy generator is an important part of the system if the equipment has to keep running.
 

Ingenieur

Senior Member
Location
Earth
Customers say that they want a UPS that will carry the load for an extended period without a generator. But what they really want is a magic box that will make electricity for 12 hours without any maintenance, and without any concern for back-to-back outages.

It was explained to me many years ago that it is usually a mistake to configure a UPS to handle an extended outage without a generator. You wind up with a big expensive bank of batteries that will need to wait for utility power to be restored before they can be recharged. You simply can't handle another outage right after recovery of utility power because the batteries haven't been able to recharge. The big, noisy generator is an important part of the system if the equipment has to keep running.

this
a genset may be a better solution
A small ups for transfer
 

mstrlucky74

Senior Member
Location
NJ
Is a single 20 ckt?
amp clamp it
120 x A = kva
I'ld bump it up 25% or next std rating

you need ~ A x 1hr ~ A-hrs at 120 vac
the UPS data sheet wil usually give % output for various time periods

you will need a decent size batt pack
12 hrs is a long time
hardwired or plug in?

equip to be backed up is plugged into 20a duplex.
 

Sahib

Senior Member
Location
India
Battery size is directly related to the power failure duration. Higher is the power failure duration, bigger is the battery size.
 