Re: UPS Load
cordial98, here is something you might want to implement in the future. Most of the larger UPS have programmable alarm set points, system load being one of them.
When a UPS is initially installed set the system load alarm to 60-to-70%. When this point is reached, it is time to plan for expansion; we kick off a EWR to cover it.
Then set the alarm point for 80%. When this point is reached, freeze the system and do not allow any more loads to be added until the expansion is completed.
Another very important step is battery PM. Most UPS use VRLA batteries which are very prone to failure and only have a life span of 5-to-10 years under ideal operating condition, which are rarely ever met. Ambient are and pilot cell Temperature?s need to be monitored around the clock with a recording device. Terminal torque needs inspected every month or two, float charge monitored, and most importantly a load test performed once a year.
Flooded batteries are much more reliable and need less maintenance, but they still need ambient air temperature monitored, terminal torque inspection, and float current monitored.
Good Luck, Dereck