UPS NEUTRAL

Status
Not open for further replies.

Abdelrazek

Member
Location
BENGHAZI
Occupation
Senior Electrical Engineer
In a three phase UPS, how to get a neutral for the single phase loads.
also why the DC source is divided by two DC/2 in the battery bank and what is its function.
Thanks
 
Dear Mr. Tom.
Thank you for your reply.
I'm talking about 3 phase UPS, the inverter output is 3 phase directly connected to the inverter.
there is no output transformer.
Is it a wye output? What does the manual say for wiring?
Can't answer on the DC source question.
 
In the larger UPS's, there is often 3Ph 3wire output only. You need a transformer to get a neutral.

The DC source arrangement is manuf specific, and Schneider for example, just arranges their DC bus that way to work with their rectifiers and inverters internally.
 