UPS output OCPD
msteiner
Maryland
I'm installing a new 300kVA UPS to replace an existing UPS of the same size. The manufacturer is proposing a unit that does not have an overcurrent device on the output circuit. The unit has two inputs--one to the rectifier, one to a static bypass switch. His argument is that the output cables are protected because the UPS electronically senses overloads and faults, and switches to the bypass circuit within a half cycle. The bypass circuit then clears the fault by way of the upstream feeder breaker. I can't find anything in the NEC that touches on this issue. Keeping in mind that the UPS is a separately derived system when in normal operation, does anyone have any thoughts regarding overcurrent protection on the output circuit?
You basically follow the manufactures instruction and design guidelines. You can certainly add a OCPD, but it wouldn't serve any purpose other than a point of failure, something a UPS is not made for.
Look at it this way, A UPS is a soft source, and could not produce enough fault current to operate your output OCPD.
Typically on a large scale UPS, the output is delta. From the output you then run to devices called PDU's for branch circuit distribution. Inside the PDU is the delta/wye transformer (SDS) where you have secondary branch circuit OCPD.
Are the input and output voltage the same or is this a 480-208Y/120V unit? Powerware's manual for 300kVA says external output overcurrent protection to be provided by user.