I need to provide 120V to a flush-mounted wiring enclosure inside of a wire closet that will contain some 120VAC powered equipment for satellite/catv distribution. The enclosure has provisions for mounting 2 duplex receptacles to the bottom of the enclosure.
The catch is that it needs to be powered from a UPS. If it was a surface mounted enclosure I would just run SO cord from the receptacle box on the enclosure to a receptacle on the UPS. But, since it's a flush mount enclosure the box for the receptacles is inside of a wall.
So, it looks like I will run NM in the wall from the enclosure to a junction box near the UPS, then transition to SO to go to the UPS. Can I just bring SO out of a cable gland on the wall plate of the junction box, or do I need a female inlet?
Is there an easier/better method? Seems like overkill to run 6-8 feet.
The catch is that it needs to be powered from a UPS. If it was a surface mounted enclosure I would just run SO cord from the receptacle box on the enclosure to a receptacle on the UPS. But, since it's a flush mount enclosure the box for the receptacles is inside of a wall.
So, it looks like I will run NM in the wall from the enclosure to a junction box near the UPS, then transition to SO to go to the UPS. Can I just bring SO out of a cable gland on the wall plate of the junction box, or do I need a female inlet?
Is there an easier/better method? Seems like overkill to run 6-8 feet.