Re: UPS protection
Mady,
The protection offered at the input to the inverter will not offer great protection for the output feeders. A breaker on the output will give more accurate protection, as the one on the input sees the losses of the UPS in addition to the load.
As a side note, MC5W, the requirements for an EPO and HVAC shutdown are not required by the NEC if the installation will comply with the first 4 chapters of the NEC.